Breaker Settings with Parallel UPS Feeds to a Bus

Status
Not open for further replies.
Hey all, so I have a system in which one bus (let's call it Bus 1) feeds one UPS, which feeds another bus (let's call it Bus 2). I have developed settings for the feeder breaker from Bus 1 to the UPS (Input Breaker 1) and the breaker from the UPS to Bus 2 (Output Breaker 1). For the sake of this discussion, let's assume those settings are correct.

The customer has indicated that they would like to install a second UPS which will be operating in parallel with the first UPS (it will have it's own set of external input and output breakers). They requested an alternative set of circuit breaker settings for two UPS's in parallel.

The UPS's are equipped with a static bypass and for the sake this topic, we're assuming that they have switched to bypass mode due to a fault on Bus 2.

The purpose of the UPS's in parallel is more for redundancy rather than load addition. Therefore the LTPU of the input/output breakers is not going to change.

However, my thoughts are that the STPU of the breaker should be reduced by half because for a fault on Bus 2, the input/output breakers will see half of the through fault current when two UPS's are in parallel. If it is not changed, then coordination with the upstream equipment could be impacted because the breaker's TCC is effectively shifted to the right by a current multiplier of two.

The instantaneous is disabled for reasons not relevant for this conversation.

Does my take on reducing the STPU by half sound reasonable? My peers have been scratching their heads but it seems pretty straight forward to me. Thoughts?

P.S. I drew out a very simplified one line to give you a visual of the layout. Also, these are 1600A breakers with an electronic trip unit. The UPS's are 1000kW to give an idea of the size.
 

Attachments

  • ups.jpg
    ups.jpg
    106.5 KB · Views: 0

Ingenieur

Senior Member
Location
Earth
what is the intent?
coordinate the ups's so only 1 trips on a downstream fault? bus 2

you have to take the ups and conductor when selecting the settings
just halfing them may not be the best setting
 
what is the intent?
coordinate the ups's so only 1 trips on a downstream fault? bus 2

you have to take the ups and conductor when selecting the settings
just halfing them may not be the best setting

Bus 1 feeds other loads than just the UPS's. The intent is that when there's a fault on Bus 2, that it trips the UPS input/output breakers before the Bus 1 main breaker. If the settings aren't changed when two UPS's are now operating in parallel. It effectively shifts the TCC to the right, correct?
 

Ingenieur

Senior Member
Location
Earth
I see your logic
you are assuming i fault at bus 2 remains the same but is ~evenly split between ups 1 and 2

I can't reach that conclusion with the limited info presented

bear in mind the Z between bus 1 and 2 is also halved
so i fault at bus will increase
how much?
estimate increase ~ 1/2(i fault bus 1 - i fault bus 2)
new bus 2 i fault ~ exist bus 2 i fault + the increase
say 20 ka at 1
15 ka at 2
increase = 1/2(20 - 15)ka = 2.5 ka
new 2 = 15 + 2.5 ~ 17.5 ka

really a new sc study should be performed
 