Shahzad
Member
- Location
- Canada and USA
- Occupation
- Electrical Engineer
Hey everyone,
I am wondering what should be the appropriate breaker frame and trip setting for 216kW, 3 phase, 400V, 50 Hz Heater. I believe the FLA would 326A, since it is electric heater, so power factor is 1.0. Bases on this, if I understand correctly, I could go maximum of 250% to select inverse time breaker trip setting, so to be realistic, if I consider 125% factor instead of 250%, I get 407A, so does this means I can get a thermal mag breaker of 410A for my 216kW load? Any thoughts?
I am wondering what should be the appropriate breaker frame and trip setting for 216kW, 3 phase, 400V, 50 Hz Heater. I believe the FLA would 326A, since it is electric heater, so power factor is 1.0. Bases on this, if I understand correctly, I could go maximum of 250% to select inverse time breaker trip setting, so to be realistic, if I consider 125% factor instead of 250%, I get 407A, so does this means I can get a thermal mag breaker of 410A for my 216kW load? Any thoughts?