Hello everyone,
I have SIEMENS Model 95 MCC, and I am trying to figure the correct required breaker sizes for my two loads as mentioned below.
Load-1: 60 HP VFD, that has input current of 88Amps. So as per NEC rule 430.122 (A): conductors need to be sized at 125% of VFD input current, thus 88x1.25=110A. So. I will be using 3C,#2 AWG having ampacity of 115Amp as I believe most of the terminal are rated at 75 deg C. Now the question is, do I need to use thermal mag breaker for short-circuit protection or instantaneous (Mag only). Should I use 125A thermal mag breaker or I should upsize it to 150A. Now, if I refer to VFD manufacturer, they recommend putting 125A fuse, but they have not mentioned anything about breaker. I am curious what size and what type of feeder breaker I should buy to feed this 88Amp, 480V, 60 hz drive?
Load-2: 60 HP across the line starter: The motor name plate is 66Amps, but if I go as per NEC table 430.250, the FLC (Full Load current) is 77Amps. I have received quote from SIEMENS vendor and he is using CED63A125 which is mag only breaker (IT) as it's a combination starter. I am curious why he has chosen 125A Inst breaker why not 2.5x66=165A (selecting 150A). I am wondering why some people use 250% Table 430.52 (inverse time) breaker selection criteria as it is confusing when it comes to starters breakers.
Thanks in advance for taking the time to respond my questions.
I have SIEMENS Model 95 MCC, and I am trying to figure the correct required breaker sizes for my two loads as mentioned below.
Load-1: 60 HP VFD, that has input current of 88Amps. So as per NEC rule 430.122 (A): conductors need to be sized at 125% of VFD input current, thus 88x1.25=110A. So. I will be using 3C,#2 AWG having ampacity of 115Amp as I believe most of the terminal are rated at 75 deg C. Now the question is, do I need to use thermal mag breaker for short-circuit protection or instantaneous (Mag only). Should I use 125A thermal mag breaker or I should upsize it to 150A. Now, if I refer to VFD manufacturer, they recommend putting 125A fuse, but they have not mentioned anything about breaker. I am curious what size and what type of feeder breaker I should buy to feed this 88Amp, 480V, 60 hz drive?
Load-2: 60 HP across the line starter: The motor name plate is 66Amps, but if I go as per NEC table 430.250, the FLC (Full Load current) is 77Amps. I have received quote from SIEMENS vendor and he is using CED63A125 which is mag only breaker (IT) as it's a combination starter. I am curious why he has chosen 125A Inst breaker why not 2.5x66=165A (selecting 150A). I am wondering why some people use 250% Table 430.52 (inverse time) breaker selection criteria as it is confusing when it comes to starters breakers.
Thanks in advance for taking the time to respond my questions.