What breaker size would I need to install if I have 208V or 240V Single Phase service
6000W/208V = 29A
6000W/240V = 25A
6000W/208V = 29A
6000W/240V = 25A
6000W/208V = 29A
6000W/240V = 25A
What breaker size would I need to install if I have 208V or 240V Single Phase service
6000W/208V = 29A
6000W/240V = 25A
So if Power Output can't change, I would size the breaker as
(6000W/208V)*125% = 36A so next size breaker is 40A.
Do you now understand that that is not true? For resistive loads, such as the heater in question, the resistance is constant, and the power is not. The related math is described above.. . . since Power was given, I have to assume it will be the same for 208V or 240V.
The unit is a radiant heater so I don't see a fan on the specifications.
But they way I approached the problem was, since Power was given, I have to assume it will be the same for 208V or 240V.
Since the specifications only gives the Watt for 240V at 6000W.
So if Power Output can't change, I would size the breaker as
(6000W/208V)*125% = 36A so next size breaker is 40A.
Not enough information given. It could be designed to use full power at both voltages.
If the element has a center tap, it could be connected to the neutral on 208 to yield the same power as it would connected to 240 line to line (no neutral connection required).
We had a thread previously about an oven that was designed this way.
True, but then it should be identified as 120/240 volts and/or 120/208 volts. Since it is identified as straight 240 volt there probably is no center tap.
What breaker size would I need to install if I have 208V or 240V Single Phase service
6000W/208V = 29A
6000W/240V = 25A
In the OP, no voltage ratings of the device were given. Only the wattage.
Then the poster speculated on the current draw at both 208 and 240.
Since the specifications only gives the Watt for 240V at 6000W.
He did clarify that the heater is designed for 240 volts.