john2016
Member
- Location
- California
- Occupation
- Electrical Engineer
I'm currently working on a Chiller replacement project. The existing chiller is fed by an existing 3P1200A breaker. On the chiller manufacturer's cut sheet it states the following for the electrical data.
Compressor Electrical Data
Power Input: 187.9 kw
Nominal Running Current: 265A
Rated Load Current: 333A
Locked Rotor Current: 366A
There are a total of 4 compressors
Chiller Electrical Data
Electrical: 460V, 3Ph, 60Hz
Power Input: 751.6 kw
Nominal Running Current: 1060A
MOP: 1391A
MCA: 1126A
The existing chiller is currently being fed by a 3P1200A breaker. Being that the MCA is at 1126A and the MOP says 1391A, am I able to reuse the existing 3P1200A breaker or do I need to upsize it to the next larger size?
If I calculate it using 175% it would equate out to 265A x 175% + 265 * 3 (additional motors) = 1258.75A
Thank you.