wwhitney
Senior Member
- Location
- Berkeley, CA
- Occupation
- Retired
Say you have a load-side generation panel with 60A of PV inverter breakers and 60A of ESS inverter breakers (and for simplicity, assume 125% of the inverter output current equals the connected breaker size in all cases). Is there something in 690 or 705 that would require the feeder connection to this panel to be protected at 120A or greater (and the feeder sized correspondingly)?
Or would it be permitted to connect just a 100A feeder, and accept the corner case risk of tripping the 100A breaker during peak conditions, when solar generation is at a maximum, the ESS is configured to offset all site loads to export all PV, and the site loads are near the ESS inverter capacity? The smaller feeder could be helpful to qualify upstream existing panels under 705.12(D) to avoid the cost of replacing them.
Or does the ESS configuration play into the answer? If the ESS is configured for "site consumption" and say the site loads are supplied by a 100A breaker, then the ESS inverter behavior should be that the combined ESS and PV inverter outputs never exceed 100A (at least, no more than the loads on a 100A breaker are allowed to).
Thanks,
Wayne
Or would it be permitted to connect just a 100A feeder, and accept the corner case risk of tripping the 100A breaker during peak conditions, when solar generation is at a maximum, the ESS is configured to offset all site loads to export all PV, and the site loads are near the ESS inverter capacity? The smaller feeder could be helpful to qualify upstream existing panels under 705.12(D) to avoid the cost of replacing them.
Or does the ESS configuration play into the answer? If the ESS is configured for "site consumption" and say the site loads are supplied by a 100A breaker, then the ESS inverter behavior should be that the combined ESS and PV inverter outputs never exceed 100A (at least, no more than the loads on a 100A breaker are allowed to).
Thanks,
Wayne