breaker size for pump

Status
Not open for further replies.
I could use help in trying to size a proper breaker for a residential sewage pump. I was told by the plumber that the motor has a "start spike" of 29 amps and the running amps are around 5.8 to 6 amps. The pump is thermally protected. Where in the NEC can I find proper sizing of the breaker for this pump. (on a side note, the variation between the start amps and running amps seems broad to me. I would think that the start amps would be closer to 19 or so but I'm going by the plumbers word.) Thanks.
 
Article 430 for motors. Take the FLA and max breaker size is 250% of that unless it turns out to be too small (i.e. it trips on start up). Most motors (ones not under a huge load when starting) will be fine on a breaker sized at 125% of the FLA (which is what the wires get sized to). Even at 250%, you're just barely looking at a 15A breaker which is the minimum for a branch circuit so it is still allowed.

Don't worry about the start spike. Breakers will ride through most of those. You could probably put 29A through a 15A breaker for a few minutes before it would trip its thermal element.
 