Given a 45 amp continuous load, 240V, single phase, (two current carrying conductors). This circuit will be pulled through a rigid metal conduit which already has eight current carrying conductors. THHN will be used for wire. Total of 10 current carrying conductors will be in the conduit. Here's my calculation.
210.19(A)1, 210.20(A), and 240.4(B) -- 45 X 1.25 =56.25 amps , choose 60 amp breaker and #4 THHN to comply with 110.14(C) for the breaker terminations.
210.19(A)2 and T.310.15(C)1 -- 45 / .5 = 90 amps, choose #4 THHN for wires when in the raceway.
Now we have a 60 amp breaker with #4 THHN wires. However, 240.4(B) also says the wires shall be protected at their ampacity, with the option of going up to the next breaker size above the ampacity of the wires.
#4 THHN in the conduit, after derating, has an ampacity of 47.5 amps, meaning the maximum overcurrent device cannot be any greater than 50 amps (240.4(B).
Upsizing the wire to a #3 THHN we have 115A x 50% = 57.5 amps, choosing the 60 amp breaker, (which is required by 210.20), is OK.
Final answer, 60 amp breaker (with 60 degree terminations), and #3 THHN. Am I correct? Nobody that I've been around ever checks, after calculating the ampacity of the wire required in the conduit, to see if the breaker size is still OK. They'll stay with the 60 amp breaker and #4 THHN.
What do you think?
210.19(A)1, 210.20(A), and 240.4(B) -- 45 X 1.25 =56.25 amps , choose 60 amp breaker and #4 THHN to comply with 110.14(C) for the breaker terminations.
210.19(A)2 and T.310.15(C)1 -- 45 / .5 = 90 amps, choose #4 THHN for wires when in the raceway.
Now we have a 60 amp breaker with #4 THHN wires. However, 240.4(B) also says the wires shall be protected at their ampacity, with the option of going up to the next breaker size above the ampacity of the wires.
#4 THHN in the conduit, after derating, has an ampacity of 47.5 amps, meaning the maximum overcurrent device cannot be any greater than 50 amps (240.4(B).
Upsizing the wire to a #3 THHN we have 115A x 50% = 57.5 amps, choosing the 60 amp breaker, (which is required by 210.20), is OK.
Final answer, 60 amp breaker (with 60 degree terminations), and #3 THHN. Am I correct? Nobody that I've been around ever checks, after calculating the ampacity of the wire required in the conduit, to see if the breaker size is still OK. They'll stay with the 60 amp breaker and #4 THHN.