what is the maximum size breaker that can be used on a seven and one half hp three phase motor that has a FLA of 24 and fed with number 10 thhn?
 
Re: breaker size

That information should be on the unit name tag.
It should list the max breaker/fuse and the minimum ampacity of the circuit conductor.
 
Re: breaker size

You can also go to 430.52 through 430.63

Roger
 