50a non continuous load. Have #6 wire run from breaker to disconnect then #8 ran rest of way. 50a breaker would work? Run about 45'
Assuming it is not nm cable then you are fine50a non continuous load. Have #6 wire run from breaker to disconnect then #8 ran rest of way. 50a breaker would work? Run about 45'
Not necessarily. Whoever may be covering themselves in the event the wiring method is NM.
Sounds like it. Most home spas get branch circuits run with NM cable.Maybe they think it would be an NM type cable being installed and not conduit/wire?