hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
I have 400A feeder breaker fed from 500kcmil conductors to Panel A.
Panel A demand load comes out to be 390A but Contractor says 390A next standard size breaker according to NEC 240.4(B) can be 400A. I dont see anything in NEC 2017 that says to upside conductor to 600kcmil? How can this be?
Panel A demand load comes out to be 390A but Contractor says 390A next standard size breaker according to NEC 240.4(B) can be 400A. I dont see anything in NEC 2017 that says to upside conductor to 600kcmil? How can this be?