Yes, so long as it meets the requirements of 240.4(B) and there isn't another section that prohibits rounding up like feeder taps (240.21). What you describe is "above the ampacity of the conductors" since your ampacity, for that conductor, after derating, is 27.5A.
From the NEC 2020 -
"
240.4 (B) -
The next higher standard overcurrent device rating (above the ampacity of the conductors being protected) shall be permitted to be used, provided all of the following conditions are met:
(1) The conductors being protected are not part of a branch circuit supplying more than one receptacle for cord-and-plug-connected portable loads.
(2) The ampacity of the conductors does not correspond with the standard ampere rating of a fuse or a circuit breaker without overload trip adjustments above its rating (but that shall be permitted to have other trip or rating adjustments).
(3) The next higher standard rating selected does not exceed 800 amperes.
"