I went and did my first load test that was a 300A square D
breaker with 350 on line side and 4/0 on load right away i say under size i take voltage and its a highleg system at the breaker its 240v on c phase 124v on a & b phase then goes to ATS and stays on c phase until it leaves ATS on B phase its all 4/0 to gen ATS & panel so I did load test and range 100 a on each phase so i tell my boss its under sized and maxed out and i can't hook up a temp 100A service for a trailer.
well 4/0 is good for 230A and you can put 300A on each leg and the trailer will only use 40 to 50A if thats true why don't we call it a 900A service
I remember asking my teacher why can't I run 3 #3 to 300Amp breaker and he said because it has the potential to put it all on one phase. so if he is right if i add the 30A to this panel it will trip if my boss is right i can put 900A on this panel before it trips or am i lost?
breaker with 350 on line side and 4/0 on load right away i say under size i take voltage and its a highleg system at the breaker its 240v on c phase 124v on a & b phase then goes to ATS and stays on c phase until it leaves ATS on B phase its all 4/0 to gen ATS & panel so I did load test and range 100 a on each phase so i tell my boss its under sized and maxed out and i can't hook up a temp 100A service for a trailer.
well 4/0 is good for 230A and you can put 300A on each leg and the trailer will only use 40 to 50A if thats true why don't we call it a 900A service
I remember asking my teacher why can't I run 3 #3 to 300Amp breaker and he said because it has the potential to put it all on one phase. so if he is right if i add the 30A to this panel it will trip if my boss is right i can put 900A on this panel before it trips or am i lost?