I am trying to size a breaker for a 3-phase 200V air-compressor motor inside of a commercial device. The nameplate of the motor reads as follows
3.0HP
200V
9.2FLA
SF 1.15
FR 56CZ
INS B
ENC Open
PH 3
THERM TYPE N
KVA CODE J
MAX AMB 40 Deg C
We are currently using a 13,13,10 breaker for the entire system , however we are experiencing widespread nuisance tripping.
The question we are trying to get to the bottom of is are we able to go up to a 15A breaker on this system. From the research I have done I have found out that for OVERLOAD protection, the cutoff is 125% FLA which is only 11.5A. The motor has built in thermal protection, but I haven't been able to find much information on thermal type N protection, so I do not know if it qualifies as adequate overload protection. From the information I found on Short-Circuit protection, the lowest rated standard breaker is 15A.
Any suggestions are appreciated. I'm a microcontroller guy so these standards are foreign to me.
3.0HP
200V
9.2FLA
SF 1.15
FR 56CZ
INS B
ENC Open
PH 3
THERM TYPE N
KVA CODE J
MAX AMB 40 Deg C
We are currently using a 13,13,10 breaker for the entire system , however we are experiencing widespread nuisance tripping.
The question we are trying to get to the bottom of is are we able to go up to a 15A breaker on this system. From the research I have done I have found out that for OVERLOAD protection, the cutoff is 125% FLA which is only 11.5A. The motor has built in thermal protection, but I haven't been able to find much information on thermal type N protection, so I do not know if it qualifies as adequate overload protection. From the information I found on Short-Circuit protection, the lowest rated standard breaker is 15A.
Any suggestions are appreciated. I'm a microcontroller guy so these standards are foreign to me.