I have a treatment panel with 2 3-phase 480V 100HP motors (112A FLA) both on variable speed drives. The max. input current on the VSDs is 112.7.
The panel has a 400A disconnect available for us to connect to.
I am figuring out the breaker size and wondering if I am doing this correctly:
Per 430.52 (c) (1): Breaker size would be 175% of the Highest motor FLA + Second motor FLA + PLC + HMI = 1.75*112+112+ 20 (approx for the PLC+HMI) = 328A.
Am I doing this correctly? Will a 350A breaker suffice?
I appreciate your help on this.