I have a brief question about breaker sizing in a PV system:
For example, a SolarEdge 10kW inverter has an output of 42A at 240V. Since the continuous output of the inverter is limited to 42A, could I use a 45A or 50A OCPD? Or do I still have to multiply it by a factor of 1.25, and use either a 55A or 60A breaker?
Thanks in advance.
-Andy