- Occupation
- Electrical Engineer
I have control transformer 1000VA, 208/120. I want to know if my breaker sizes are correct as per UL508A. Primary side, 1000/208 *250/100=12A. What should be the size of breaker 10A or 15A on primary side? On secondary side, 1000/120 * 125/100=10A. Is 10A breaker ok on secondary side? Thank you,