I have jockey pump controller service rated fed from fire pump circuit which is taped ahead of main service disconnect.
The jockey pump is 3/4 hp, 2.5FLA and 27.4A LRC.
The engineer has sized the fuse inside the jockey pump based on LRC and says he is providing the fuse. The fuse size is 30A.
My concern is based on NEC 2017 Section 695 info note jockey pump install need to comply with 430.
So would the jockey pump service rated fuse of 30A oversized or it is acceptable to size it based on LRC? Also would not jockey pump need overload protection?