Z zooby Senior Member Location Indiana Occupation maint. electrician Nov 5, 2025 #1 Scenario--- padmount to ATS -"normal power" lands on 200A CB. 150A CB at generator to ATS emerg. power. I not saying this is wrong but curious why not use a 200A at the generator? Thoughts ?
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Nov 5, 2025 #2 I would think the 150 amp was designed to protect the generator (as well as the load size conductors). What kw is the generator ?
Z zooby Senior Member Location Indiana Occupation maint. electrician Nov 5, 2025 #3 augie47 said: I would think the 150 amp was designed to protect the generator (as well as the load size conductors). What kw is the generator ? Click to expand... prettysure this one is a 500kw. It has other buildings/loads on it.