He only asked about setting the magnetic trip elements for motor starter breakers.
That is covered in 430.52
Synopsis:
If you have a Thermal-Mag breaker, most applications will fall under 452.C.1 exception 2(c) because standard Thermal-Mag breakers without adjustable mag trips will not stay in under typical motor starting current. If the Mag Trips are adjustable, use the table and exception 1
If you have a Mag-Only breaker (a.k.a. MCP), i.e. what is usually provided as part of a listed Combination Starter, use 452.C.3, exception 1