Question came up the other day and I cannot find an answer. When installing a whole-house generator one often ends up re-routing the service conductors to the new main breaker in the service rated transfer switch. Then new feeder conductors are routed from the load lugs of that new switch to the existing main breaker of the house panel (which is now....in essence....a sub panel after the bond is removed and the grounded conductors are separated from the grounding conductors, etc.)
So....is there any code violation that arises when feeding, say, a 200A MCB in a panel with a feeder that is already protected by a 200A breaker up stream? I am thinking it's fine, but would like to ask the group for some re-assurance...or correction if I'm missing something.
So....is there any code violation that arises when feeding, say, a 200A MCB in a panel with a feeder that is already protected by a 200A breaker up stream? I am thinking it's fine, but would like to ask the group for some re-assurance...or correction if I'm missing something.