Circuit breakers are tested per NEMA, ANSI, NETA and the particular manufactures specifications
Breakers are high current tested for long time and instantaneous pick up
Meggered-Insulation resistance test.
Ductored/micro ohmed, DLRO (contact resistance measurement.
Interesting I understand that NETA just uses NEMA/ANSI standards.
Testing breakers is not that easy if you use factory testing techniques. Their equipment cost tens of thousands of dollars. I have the opportunity to test breakers at an actual factory test bench use to test breakers returned under warranty. I find it interesting that this type of equipment can be affordable in the field. NEMA AB4 was the only field testing method that I would accept as a valid field test.
NEMA AB4 is the "Guidelines For Inspection And Preventive Maintenance Of Molded Case Circuit Breakers Used In Commercial And Industrial Applications."
This publication illustrates the test setup.
The only includes a time current trip test is at 300% of rated continuous current of the circuit breaker trip times are as included per table 5-3.
5.6.4.1:For instantaneous a runup and pulse methods can be used. When using the run up method if done incorrectly it can destroy a breaker. As such testing one pole at a time and limiting the run up time between 2-5 sec useing an ammeter.
5.6.4.2:The pulse method uses an oscilloscope where the pulse is 5-10 cycles.
5.7 Covers the hold in test which is a test to varify that the breaker is capable of carrying its rated current.
And last, contact resistance test is irrelevent. Such a test may be used as a way to compare the resistance of the contacts. The are no go or no go values as some would like.
5.4.1 States:The millivolt drop of a circuit breaker pole can vary significantly due to inherent variability in the extremely low resistance of the electrical contacts and connectors. Such variations do not necessarily predict unacceptable performance and SHALL NOT BE USED AS THE SOLE CRITERIA FOR DETERMINAION OF ACCEPTABLILIY.
That's straight from the "NEMA AB4" publication.
I worked as an breaker application engineer for a major manufacturer and have been often amused by the so called field verification test.