We have a commercial job with three subpanels. The MDP was originally supposed to have 400A, 225A, and 100A feeder breakers for the subpanels. But a change was made very early in the process, the 400A subpanel was changed to 225A.
So, they sent me a submittal with all the information, and I neglected to check it in time. When I finally looked at the submittals 5 months later, I saw they had changed the subpanel, but had not changed the feeder breaker. I immediately contacted them and asked if the 400A breaker could be changed to a 225A one, and they thought it could, but they never got back to me and now it's been two more months, and the customer will be ready to install this stuff soon. I'm trying to deal with this and I see the two breakers have two different frame sizes, so maybe we couldn't change the 400A breaker to a 225.
1 Lighting Panelboard, ReliaGear RQ
Marks: MDP
1 Section(s), NEMA 3R Cabinets
600 Amps, 3 Phase 4 Wire 208Y/120V, 50/60 Hz
Minimum Interrupt Rating: 22kA Fully Rated
Incoming Feed: Bottom
Surface Mounted
12 Circuits
UL67 / CSA C22.2 No. 29 Certified
cULus Certified
Height: 76.5 Inches; Width: 20 Inches; Depth: 6.21 Inches
1 600 Amps Main Lugs
1-lug/phase 2-cable/lug 2/0 -500 kcmil
Main Option Details
1 Copper Bus Heat Rated
2 Ground-Box bonded TGL2
1 Ground main lug TGL20
1 100% Rated Neutral
1 NEMA 3R Cabinets
Feeders
1 Breaker Device 400 Amps 3 Poles XT5N400
1 TMA
1 Breaker Device 225 Amps 3 Poles A2N250
1 Breaker Device 100 Amps 3 Poles THHQB
1 Breaker Device 20 Amps 1 Poles THHQB
Modifications
1 Nameplates
1 Interior: AQF3126MBX AXQ3G1B7
1 Box: AB763
1 Front : NONE
I see they have adjustable trip points, but I'm not sure if it can be set down that low. Can the above-listed 400A breaker be adjusted to 225A? If the 400A breaker can be adjusted to 225A, what is the procedure to make sure the adjustment complies with code? I found this thread saying something about a seal on the breaker: https://forums.mikeholt.com/threads...400-amp-feeder-to-distribution-panel.2566662/ I'm just not sure what that is, never having worked with these very extensively.
So, they sent me a submittal with all the information, and I neglected to check it in time. When I finally looked at the submittals 5 months later, I saw they had changed the subpanel, but had not changed the feeder breaker. I immediately contacted them and asked if the 400A breaker could be changed to a 225A one, and they thought it could, but they never got back to me and now it's been two more months, and the customer will be ready to install this stuff soon. I'm trying to deal with this and I see the two breakers have two different frame sizes, so maybe we couldn't change the 400A breaker to a 225.
1 Lighting Panelboard, ReliaGear RQ
Marks: MDP
1 Section(s), NEMA 3R Cabinets
600 Amps, 3 Phase 4 Wire 208Y/120V, 50/60 Hz
Minimum Interrupt Rating: 22kA Fully Rated
Incoming Feed: Bottom
Surface Mounted
12 Circuits
UL67 / CSA C22.2 No. 29 Certified
cULus Certified
Height: 76.5 Inches; Width: 20 Inches; Depth: 6.21 Inches
1 600 Amps Main Lugs
1-lug/phase 2-cable/lug 2/0 -500 kcmil
Main Option Details
1 Copper Bus Heat Rated
2 Ground-Box bonded TGL2
1 Ground main lug TGL20
1 100% Rated Neutral
1 NEMA 3R Cabinets
Feeders
1 Breaker Device 400 Amps 3 Poles XT5N400
1 TMA
1 Breaker Device 225 Amps 3 Poles A2N250
1 Breaker Device 100 Amps 3 Poles THHQB
1 Breaker Device 20 Amps 1 Poles THHQB
Modifications
1 Nameplates
1 Interior: AQF3126MBX AXQ3G1B7
1 Box: AB763
1 Front : NONE
I see they have adjustable trip points, but I'm not sure if it can be set down that low. Can the above-listed 400A breaker be adjusted to 225A? If the 400A breaker can be adjusted to 225A, what is the procedure to make sure the adjustment complies with code? I found this thread saying something about a seal on the breaker: https://forums.mikeholt.com/threads...400-amp-feeder-to-distribution-panel.2566662/ I'm just not sure what that is, never having worked with these very extensively.