every timeSevere under voltage when the lightning strike takes something out suddenly?
What do you mean by 'in the area'? There is a big difference between 10 miles and 100 feet.main breaker (1200A, LI trip, no ground fault detection) in service panel is tripped whenever there are lightnings in the area,
panel has no spd, does anyone has any ideas why? surges?
noDoes the breaker have under- or overvoltage trip protection?
"in the area" is where the building has panel located.What do you mean by 'in the area'? There is a big difference between 10 miles and 100 feet.
How often has this happened?
What is the complete catalog number of the breaker?
If you are talking about lightning strikes to the building itself, your first step should be a lightning protection system."in the area" is where the building has panel located.
Here is breaker catalog # Eaton NGS212033E. Thought breaker only tripped under overload or short current condition, lightning sounds like over voltage to me...If you are talking about lightning strikes to the building itself, your first step should be a lightning protection system.
If you are talking about lightning strikes to nearby buildings, their surge currents may be flowing through your grounding system. Have you had your ground and bonding tested with a 3 or 4 point tester?
If you are talking about lightning strikes on or nearby your utility distribution system, you should be checking your grounding bonding and adding multiple levels of surge suppression.
When testing boring do not forget all underground piping, such as fire systems, gas piping, and process piping run between buildings.