Ken9876
Senior Member
- Location
- Jersey Shore
I have a bit of a problem with a 100 amp 480 volt Westinghouse breaker tripping when transfering back from generator power. L1 49A, L2 56A, L3 48A, voltage is good. One thing I belive that might be causing this problem is awhile back they added more heat to this circuit. There are three transformers feed off this breaker, serving rec. lighting and some heating loads, no motor loads other than what's in the heaters. I was there last night and had to dump two of the breakers feeding transformers, to get the ATS to transfer back without tripping. The transfer switch is an old Allen Bradley ATS. Took some inrush reading today with a Fluke 434 the inrush goes upto 400 amps, but it does the same thing when transfering to generator and that breaker holds. Any thoughts?