Hi All,
Recommissioning an old Control Cabinet and retrofitted it with some new control gear. I'm looking to put it back into use, however when i turn off the isolator on the Control Panel, it trips the 16A Breaker for the Socket its plugged into.
Checked for Ground Faults and Short-circuits, everything seems to be fine. Isolator is 4 Pole (3Ph + N), Plug wiring looks good.
Cabinet has a Siemens Simanics V20 VFD and Logo8 Controls, motor isnt running when powered down so there shouldn't be any inductive kickback. However when I E-Stop the machine before turning off the isolator, which in turn cuts power to the VFD via the branch contactor, the breaker doesn't trip.
Trip Switch is a Hager ADM420c B20.
Any suggestions?
Thanks.