breaker tripping ?

Status
Not open for further replies.

papa

Member
Location
South Carolina
480 volt 30 amp breaker for parking pole lights is tripping after about one hour. Lights are 480 and feed though a contactor . Ohmed each leg to ground and phase to phase seems ok. Amps are L1-6, L2-7, L3-6. Any suggestions?
 

SG-1

Senior Member
1.You could have a bad breaker. ( Might try a fall of potential test across the breaker. )

2. You may need to continously monitor the current to the lights, because at some point it is great enough to trip the breaker.

3. Megger Time. The conduits could be flooded.

4. The insulation in one of the lights may be breaking down when it reaches a certain temperature. ( Continously monitor the current to see which phase(s).)
 

jeremysterling

Senior Member
Location
Austin, TX
1.You could have a bad breaker. ( Might try a fall of potential test across the breaker. )

2. You may need to continously monitor the current to the lights, because at some point it is great enough to trip the breaker.

3. Megger Time. The conduits could be flooded.

4. The insulation in one of the lights may be breaking down when it reaches a certain temperature. ( Continously monitor the current to see which phase(s).)

I saw this happen where the answer was: 3. flooded conduits.
 