Actually, most of them I don't. It might only leave the bin on the truck where it's kept maybe once a week. I'm telling all you service guysl... if you aren't using a megger to speed up your troubleshooting on certain things, you're really missing the boat productivity wise. Even if productivity isn't your main motivator, and $$'s are, it will also permit you to more easily identify in quantifiable terms equipment and conductors that should be condemned and replaced. There are certain calls, like intermittant breaker tripping, where the megger check is the right thing to do. Spent my afternoon just today at a 6-unit apartment building that had a bad water leak, and the fire department shut the power off until an electrician checked things out (that was me). Here we are, talking about not working Saturdays in another thread, and I'm taking branch circuits out of the panel and meggerring them out. I got about 80% of the building turned back on, and I have about 6 or 8 circuits total that need investigated further one day next week. Today, I was the megger hero to 6 apartments worth of people who would have otherwise been displaced. How would an electrician without a megger have checked this stuff out? Turned the breakers back on, and waited to see if something tripped or erupted in flame? :wink: