Background information:
I have an existing factory that has a switchgear that is rated for 65 kA for its bus. However, some of the breakers are only rated 25 kA inside this switchgear.
That might not be a problem, but with easypower arc flash software, I show a 27 kA short circuit on the switchgear bus in a faulted situation. The main transformer is 500 KVA with 2% impedance. Infinite bus calculation would be around 30 kA. so the 27 kA sounds reasonable since all the utility short circuit info was entered correctly from the utility company.
Actual question:
Is it against code to put a breaker that is rated less than 65kA on a bus that is rated 65 kA?
My guess is that a 35kA breaker would work just dandy, but I prefer not to guess.
Incidentally, first time I've seen a 2% impedance on a main transformer. Super efficient, but high kA ratings for your equipment.
I have an existing factory that has a switchgear that is rated for 65 kA for its bus. However, some of the breakers are only rated 25 kA inside this switchgear.
That might not be a problem, but with easypower arc flash software, I show a 27 kA short circuit on the switchgear bus in a faulted situation. The main transformer is 500 KVA with 2% impedance. Infinite bus calculation would be around 30 kA. so the 27 kA sounds reasonable since all the utility short circuit info was entered correctly from the utility company.
Actual question:
Is it against code to put a breaker that is rated less than 65kA on a bus that is rated 65 kA?
My guess is that a 35kA breaker would work just dandy, but I prefer not to guess.
Incidentally, first time I've seen a 2% impedance on a main transformer. Super efficient, but high kA ratings for your equipment.