Jason W
Member
- Location
- Portland, Maine
- Occupation
- Solar design and installation
I have an installation with 13 GoodWe single phase inverters and two 400 amp services with a pad mounted 167kVa transformer. The inverters are all 11.4 k, except for one which is 7.7 k. One 400 amp panel has six 11.4 k inverters and the other has six 11.4 k and one 7.6 k.
My problem is that the breakers for each inverter are overheating and tripping. We have verified that all the wire sizing is correct, the breakers are rated for backfeeding and correctly sized, all terminals are torqued to specifications and the grounding is properly done. The inverters are never going over their rated maximum amperage on the AC output so the breaker trip is happening because of excessive heating. We have shot both panels with IR camera and the temp on the breakers goes from ambient (around 75 degrees F) to over 160 degrees in less than an hour on one panel; on the other panel it goes up but not as fast or as high and breakers trip.
When the inverters are at full power, both panels hum and vibrate as do the disconnects between the main panels and the meters. The big difference between the panel B that has the heating problem to an extreme and the panel A that heats, but much less, is the length of the AC conductor runs. The inverters that heat the most are the ones with the shortest AC runs and the ones at the top of the bus bar, in both panels.
I suspect that the problem is caused by harmonic distortion but what is casing the HD is the mystery. Maybe induction--the 5 inverters that heat the most have ac conductors in non-metallic liquid tight and run right next to each other across the mounting board to the panel. Maybe it is HD from the inverters, but GoodWe claims to have multi-inverter installations in other locations that are not having this problem.
Would love any ideas about the cause that you can think of.
My problem is that the breakers for each inverter are overheating and tripping. We have verified that all the wire sizing is correct, the breakers are rated for backfeeding and correctly sized, all terminals are torqued to specifications and the grounding is properly done. The inverters are never going over their rated maximum amperage on the AC output so the breaker trip is happening because of excessive heating. We have shot both panels with IR camera and the temp on the breakers goes from ambient (around 75 degrees F) to over 160 degrees in less than an hour on one panel; on the other panel it goes up but not as fast or as high and breakers trip.
When the inverters are at full power, both panels hum and vibrate as do the disconnects between the main panels and the meters. The big difference between the panel B that has the heating problem to an extreme and the panel A that heats, but much less, is the length of the AC conductor runs. The inverters that heat the most are the ones with the shortest AC runs and the ones at the top of the bus bar, in both panels.
I suspect that the problem is caused by harmonic distortion but what is casing the HD is the mystery. Maybe induction--the 5 inverters that heat the most have ac conductors in non-metallic liquid tight and run right next to each other across the mounting board to the panel. Maybe it is HD from the inverters, but GoodWe claims to have multi-inverter installations in other locations that are not having this problem.
Would love any ideas about the cause that you can think of.