Re: breakers
elect36,
While the current that flows when a short circuit occurs is large, it is not "any amount", or as I take you to mean, unrestrained or infinite.
The power company transformer secondary supplying the current has a resistance. It is small, but it is an important resistance. The service entrance and service drop/lateral conductors have a small resistance also. And the branch circuit conductors have a small resistance. The arc at the short (if there is an arc) also has a resistance.
All these little resistances add together to be the limit. A real world short is not often a very low resistance bolted short. So, the conditions of the actual short also help to reduce the peak current.
The contacts in the circuit breaker are designed to open and extinguish the arc created by interrupting the large current that flows during a short circuit. The common breaker today is rated 10,000 amps interrupting capacity.
A 20 amp 125 volt circuit in a single family dwelling will generally have a available short circuit of a few hundred to a few thousand amps. That allows the breaker to extinguish the arc when it opens.
If the arc can't be extinguished, the arc continues and burns things up.