Re: Breakers
Brian,
We do new work, not maintenance/testing, so some of this info is new to me (I probably should know it already, but... what can I say?
). But we do have to occasionally trouble-shoot problems with new equipment or on warranty calls, so I need to understand this maintenance/testing aspect as well.
If I understand what you are saying, if (at full load) I measure the voltage across one phase of a circuit breaker (from the line (bus) connection to the load lug) and I measure over 20 millivolts, then there is enough internal resistance to indicate bad contacts or other problems within the breaker and it should be replaced. Is that correct?
This same procedure could be used for a disconnect switch (measure from the line-in lug to the load lug, or even just across the knife switch contacts). Again, any voltage over 20MV would be bad, indicating that there is a problem?
This same procedure could be used for checking busbar connections or other mechanical connections. Over 20MV would indicate that the connection needed fixing?
Of course, all measurements must be made under full load conditions, and you would have to check each pole of a circuit breaker, switch or other multiphase device.
Am I understanding you correctly?
What conditions raise this measurement to 100 Millivolts before a problem is indicated?