Re: breaking the neutral in a motor starter
It's hard to answer your question if you don't describe the motor starter application. You just indicated "overload condition" and made not mention of how the motor was actually controlled.
But....this is a guess.
On a single phase 120v motor where you have a line and neutral it is quite common to use a 2p starter, either manual or magnetic where both the line and neutral are opened and closed simultaneously to control the motor. The overload will also open both line and neutral contacts in response to an overload condition.
Their's nothing wrong with this as long as the neutral is opened and closed at the same time as the line is. However, the neutral does not need to be broken as a single pole would do.