luckylerado
Senior Member
- Location
- Lake of the Ozarks
Been asked to comment on an installation of several sets of 480V Ckts ran in J-Hooks. The cables are failing megger testing and I am doing a kind of autopsy on the install. One of the things jumping out at me are the J-hooks. These are in an underground concrete trench meant for electrical feeders with the J-hooks attached to the walls. I have done some searching and I believe certain sheathed cables may be installed this way but I have no reason to believe that individual bundles of THWN-2 would be compliant. Can anyone offer a code reference that clearly states this is not allowed. This is not something I would have even considered doing but if it is compliant then I will just shake my head concede.