Aleman
Senior Member
- Location
- Southern Ca, USA
I have been tasked with bringing several old control panels up to code. None of these will be listed. All will have arc flash studies and most of them already have.
Per art 409 NEC I know I need to establish SCCR for all panels and label with the value.
Wire colors are not per UL508A but it would be a lot of work to rewire, especially since these will all be replaced within 2 years. I am not convinced that I need to rewire
any of this as long as grounds are green. The DC colors vary, black, white, red. Most of the line voltage is black or colored per ac voltage BOY etc.
What I plan to do is make sure everything has proper circuit protection as per NEC guidelines, and get the SCCR's. In your opinions do I need to rewire with UL508A colors
to satisfy basic code requirements?