As mentioned, it will depend on your application. If you asking about MWBC disconnection requirements see 210.4 and 240.15(B). Handle ties are fine for this.are circuit breaker handle ties still acceptable, or do I need to replace breaker with multipole common trip brkr?
I meant to say "line-to-line" loads here.Automatic opening (tripping) for line loads require common trip.
Handle ties are permitted for 240 volt line to line loads on a 120/240 volt system and for 208 volt line to line loads on a 208Y/120 volt system. 240.15(B)(2) & (3)I meant to say "line-to-line" loads here.
What specifically requires internal common trip?Handle ties are permitted for 240 volt line to line loads on a 120/240 volt system and for 208 volt line to line loads on a 208Y/120 volt system. 240.15(B)(2) & (3)
Equipment with line to line along with line to neutral, and for line to line loads on circuits with a voltage to ground that exceeds 120 volts. Or in other words, all circuits not covered by 240.15(B)(1) through (4).What specifically requires internal common trip?
Interesting, I was not aware of that. I never looked closely enough at the wording.Handle ties are permitted for 240 volt line to line loads on a 120/240 volt system and for 208 volt line to line loads on a 208Y/120 volt system. 240.15(B)(2) & (3)