grant said:
I can't remember on those old panels if the line goes to the tip or the shell of the screw-in fuse holder . . .
It's always line to tip.
electricman2 said:
The screw shell is on the load side of the fuse. If there is a direct short somewhere to ground on the load side of the fuse that blows, then there will be 120V between the shell and the load terminal below it. I believe the two fuses on the left are fed from the same side of the line.
Yes, the shell is on the load side, and (should be) solidly connected to the load terminal. I should be reading nothing between them, but 120v between either one and the line side, i.e., the tip.
I'm only looking at a single terminal, so the same-or-opposite-phase issue is not relevant.
don_resqcapt19 said:
There should always be zero volts between those two points as they are physically connected.
Yeah.
al hildenbrand said:
The screw shell can get torn, or worn, loose from the load side bar that extends to the branch circuit terminal screw.
I'm leaning that way myself. Unfortunately, there are non-removable tamper-proof adapters in there.
If there is also 120 volts between the terminal and the neutral, the circuit is being backfed from another circuit.
I will be going back, probably tomorrow, and will check. It may be more complicated than this, however; this circuit is presently out of order, which is what led to me being called. A back-feed should be poroviding power.
This is probably not the original service, but in spite of that, there are two separage 2-fuse switches alongside. I have a feeling I'm going to find something weird that should have malfunctioned a long time ago.
In the it's-always-something category: I am giving a service-change proposal, but they will be adding onto the house this spring, the panel is on the rear of the house, and it would be best to do the service at the same time.
cschmid said:
..can you get us a pic of the panel..
If I think I need more input tomorrow, I will, if I remember . . .
"Try to remember . . . the kind of September . . . "
frenchelectrican said:
Larry.,,
I dont know if this will work but screw in the light bulb
Marc, I've been doing that for years, even with a rubber pigtail lampholder in breaker panels. (And I always connect the line to the center contact.

) I'm old-school, too. Well, compared to the majority here, I think.