UPMICHIGAN
- Michigan
Hello
I am trying to understand why I am detecting voltage on my broken delta and why sometimes this voltage rises high enough to operate my relay and trip my generator on ground fault
My system is a 4160 volt ungrounded delta and we use a Wye grounded/broken delta PT arrangement for ground fault detection
A couple questions I have
There are absolutely no line to neutral loads, but will different line to line voltages seen by the wye/broken delta cause zero sequence voltage to be detected? For example if AB volts is different then AC volts is different then BC volts does that mean A-GND is different then B-GND is different then C-GND?
I’m confused why I have any voltage to ground at all in the broken delta to begin with and why it sometimes rises too high.
Am I right that under normal conditions 0 volts on broken delta?
Even if line to line voltage is different that doesn’t necessarily mean line to ground voltages aren’t equal, correct?
Could my problem not be voltage magnitude difference but voltage angle difference?
Thanks