Sorry, I probably asked this in the wrong thread yesterday:
We are installing a 20 HP 115 VDC motor in a Class 1, Div 2, Group D building. Because of the voltage, we are only able to refurbish an existing TEFC motor, so we don't have an explosion proof one. This motor has brushes, if they are in the enclosure thats fan cooled does this allow the motor to go in the hazardous area? Or since the brushes create sparks, we would need an explosion proof enclosure?
Reading NEC 501.125(B)'s paragraph "In Class 1, Div 2 locations, the installation of nonexplosion proof enclosed motors such as squirrel-cage induction motors WITHOUT BRUSHES or other arc producing devices are permitted" leaves me to believe i'm gonna have to get an explosion proof one. The terminal housing, however, is explosion proof with epoxy sealing for the motor leads into the enclosure.
We are installing a 20 HP 115 VDC motor in a Class 1, Div 2, Group D building. Because of the voltage, we are only able to refurbish an existing TEFC motor, so we don't have an explosion proof one. This motor has brushes, if they are in the enclosure thats fan cooled does this allow the motor to go in the hazardous area? Or since the brushes create sparks, we would need an explosion proof enclosure?
Reading NEC 501.125(B)'s paragraph "In Class 1, Div 2 locations, the installation of nonexplosion proof enclosed motors such as squirrel-cage induction motors WITHOUT BRUSHES or other arc producing devices are permitted" leaves me to believe i'm gonna have to get an explosion proof one. The terminal housing, however, is explosion proof with epoxy sealing for the motor leads into the enclosure.