UL Listing AALZ Pg 47 08 White Book
Distribution and Control Equipment Terminations
Most terminals are suitable for use only with copper wire. Where aluminum
or copper-clad aluminum wire can or shall be used (some crimp terminals
may be Listed only for aluminum wire), there is marking to indicate
this. Such marking is required to be independent of any marking on
terminal connectors, such as on a wiring diagram or other visible location.
The marking may be in an abbreviated form, such as ??AL-CU.??
Except as noted in the following paragraphs or in the general Guide
Information for some product categories, the termination provisions are
based on the use of 60?C ampacities for wire size Nos. 14-1 AWG, and
75?C ampacities for wire size Nos. 1/0 AWG and larger, as specified in
Table 310.16 of the NEC.
Some distribution and control equipment is marked to indicate the
required temperature rating of each field-installed conductor. If the equipment,
normally intended for connection by wire sizes within the range
14-1 AWG, is marked ??75C?? or ??60/75C,?? it is intended that 75?C insulated
wire may be used at full 75?C ampacity. Where the connection is
made to a circuit breaker or switch within the equipment, such a circuit
breaker or switch must also be marked for the temperature rating of the
conductor.
A 75?C conductor temperature marking on a circuit breaker or switch
normally intended for wire sizes 14-1 AWG does not in itself indicate that
75?C insulated wire can be used unless 1) the circuit breaker or switch is
used by itself, such as in a separate enclosure, or 2) the equipment in
which the circuit breaker or switch is installed is also so marked.