I cannot find a code on this, and electrically I do not know the right way to handle this; doing a remodel on a old house with a Bryant panel, they have three split breakers with three old 12-3 romax (no ground) coming off of the split breaker (Edison circuit); does it matter that both feeds derive from the same split breaker, no way to install two poll breaker for Edison circuit, no room
 

hbiss

EC, Westchester, New York NEC: 2014
Location
Hawthorne, New York NEC: 2014
Occupation
EC
does it matter that both feeds derive from the same split breaker,
Yeah it does. If both circuits of a 3 wire cable are on the same phase (as is normally the case when supplied by a tandem breaker), the common neutral can be overloaded. The solution is simple without changing breakers. Simply re-arrange the 12/3s by moving the hots to other side by side breakers as necessary so that the hots of each 12/3 are on separate phases. You can use the tandems as necessary to supply the circuits you moved.

-Hal
 

Electromatic

Senior Member
Location
Virginia
Occupation
Master Electrician
Another problem here is that current code requires mulit-wire (Edison) circuits to be protected with handle-tied breakers. You may want to look at Eaton's BR quad breakers.
1728648217940.jpeg
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Note: Both halves of tandem breakers are on the same phase.

Put the blacks on one phase and the reds on the other phase.
 