BTU Loading Single phase

Status
Not open for further replies.

John Thomas

New member
BTU loading is watts time 3.41. On a 20 amp single phase circuit to an appliance I've clamped 14 amps. The nuetral of the same circuit clamps 4 amps. Is the actual BTU loading based on load amps or is the nuetral/hot difference times 3.41 the actual BTU loss?
 
BTU loading is watts time 3.41. On a 20 amp single phase circuit to an appliance I've clamped 14 amps. The nuetral of the same circuit clamps 4 amps. Is the actual BTU loading based on load amps or is the nuetral/hot difference times 3.41 the actual BTU loss?
The neutral/hot difference had better be due to the appliance being a 120/240v device, or that 10a on another line sharing the neutral.
 
John,

This is getting interesting.

You start with 14A,
locate where 4A returns,
and still are looking for the last 10A ?

What are the possibilities?

Hope you enjoy this professional forum.
...
 