Hello All,
One engineer designs a 7.5kVA 240-208 1P, 3W Buck Boost transformer with 225A breaker, #4/0 CU on the 240V primary side and 225A breaker, #4/0 CU on the 208V secondary side. The 225A main breaker of the panel on the secondary side is within 10ft of the transformer.
Per section 450.4, the OCPD shall be rated not more than 125% of the rated full load input current of the autotransformer.
To me, the rated full load input current is the primary current which is 7.5/.24 = 31.25A. The max OCPD is 39.06A or 40A.
The engineer said the Buck Boost transformer can produce: 7.5/(.24-.208) = 7.5/0.032 = 234.375A.
Can you tell me who is right?
Thank you.