Buck & Boost Transformer on a welder

Merry Christmas

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Anyone aware of any problem using a buck n boost transformer on a welder.
Customer has a welder (unknown type) & manufacturer insists it must have a 240v input. His system is 208. Exact welder current is unknown but supplier asks for a 50 amp ciruit. B&B selected has a 62.5 amp rated secondary current.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I've installed a few over the years, mostly on tanning beds, bu was curious about them on welders due to the nature of the load.
 

junkhound

Senior Member
Location
Renton, WA
Occupation
EE, power electronics specialty
manufacturer insists it must have a 240v input.

WHY?? Only reason I could se is if it is a welder with high frequency stabilization If that the case, you could add a smaller internal boost transformer for that circuit. zOr even just add in a 28V secondary in series with the internal cirduit.

Of course, no longer listed, etc. etc.....
 