I am going to wire a air compressor that has a tag 10 hp 230/460 volts 3 phase.the service is 120/208 3 phase so i will need to use a 24 volt boost transformer at .75 kva. it will be connected open delta requiring two transformers and i understand how to do that.The motor amps are 28 on table 430.250 and can be increased by 250% if using a circuit breaker.So a 70 amp breaker at the panel can be used to feed the motor. When I install the boost transformer will it still be protected if using a 70 amp circuit breaker?do i need any protection on the secondary besides the motor starter?