wilbur101
Member
Ok, I've got a problem. Several actually, but I am only looking here for help with the technical one. Anyway, I am working on an expansion project for an industrial manufacturing client in Virginia. The client has an existing distribution and wants me to use a 480V, 3phase 1200A feeder from an existing substation for a feed to a new building. The building is approximately 800 feet away. I do not like doing this, but this is what the client is mandating. There will be a voltage drop of about 5-6%. The client is also locked into using Square D equipment. The client wants to use a Buck/Boost transformer to resolve the voltage drop problem. The client's design has the 1200A feeder going to a 1200A I-Line panel and then an 800A breaker in the I-Line panel feeds out to a 500kVA transformer. There is a second 800A breaker in the I-Line panel that feeds another 500kVA transformer. Has anyone ever done anything like this? Does Square D make a Buck/Boost transformer large enough (I can't find one and the local rep is just shy of useless on this topic)? Square D literature seems to indicate that 2 transformers will be required for each buck/boost - this seems like it will require a huge amount of space. I always thought buck/boost transfromers were used for smaller loads or dedicated loads and not building feeds. Any help or advice is greatly appreciated.