Buck/Boost Wiring method

Status
Not open for further replies.

MFH

Member
Location
USA
Occupation
Journey Electrician
we are installing buck transformers for several amusement rides in an out door location, any recommendations . Running liquid tight between them seems a bit messy (what do I know).
I’m sure there’s another way and space is one problem. Thanks
 
Yes they are permanent . And apologize, because we are boosting the utility that changed from 240 delta to a 208 wye . Everything would love a little high voltage at this point. Some of the older rides are straight 230v . Also the area is seasonal and tends to brown around 4pm to 7pm , (that’s a different elephant). It’s a bit to keep it straight some times because on top of it , there are rides imported from Europe that run on 400 volts . The boost transformers are 15% I believe. Three small ones . We are going to run liquid tight between them. They are exposed outside . I’m just wondering if I’m missing something that’s obvious to someone else’s eyes. A small trough could be used to dress it up a bit, but the location is on the back or side of a hefty post that has a disconnect on the front of it . We are installing the group of three vertically to try and keep them hidden as much as possible , but also accesible. No one wants to see our work , but enjoy the benefits of it. I could be wishing there is another way and is not feasible. I figured why not ask a group that are the ones that are going to judge it the most. I always look at other installations of equipment when out and wonder why they did it a certain way. Thanks for any input and time . Will post pictures of install when completed. Mike
 
I always found that using a trough is the easiest way to make the many splices when using Buck Boost transformers. We were taught in Vo Tech class that it's better to use 3 buck Boost transformers rather then two for better voltage regulation on three phase. Only need one Buck Boost for single phase loads. They make nice NEMA 4 troughs for outdoor use. I would use sealing lock nuts rather then Meyer hubs and short conduit nipples. All of the Buck Boost transformers that I used had two primary & two secondary windings so you would have to splice 24 wires ( not counting grounds ) when using 3 of these transformers.
 
Last edited by a moderator:
I agree with garbo in a wireway is often an ideal methiod but your having to mount them vertically poses a challenge on wireway,
 
That’s the way I was leaning ,we have the three transformers , but as augie47 mentioned it’s the vertical aspect. I know they make gasket
ed trough but not sure if it’s rated for vertical install . Can’t think of it off hand it’s rated 4I or simular for dust and possibly gases. I was even thinking using condulets Instead of the flex, I don’t know , it has its place but flex seems cheesy to me.
 
i guess that’s where I wanted to go with this . Manufacturers make solutions to situations like this and I might not know about it,but someone out there does . Or it’s not a profitable situation and it stays the same forever, my favorites (plug mold) still a pain to install and hasn’t changed for my 30 years.
 
we are installing buck transformers for several amusement rides in an out door location, any recommendations . Running liquid tight between them seems a bit messy (what do I know).
I’m sure there’s another way and space is one problem. Thanks
I don't have an issue with liquid tight of some sort. Who cares what it looks like. it is functional.
 
What about using two T-condulets and one LB (or LR or LL) to connect the vertical stack?

All of the connections can be made within the transformer wiring compartments.
 
What about using two T-condulets and one LB (or LR or LL) to connect the vertical stack?

All of the connections can be made within the transformer wiring compartments.
I think it might depend on the circuit size. On larger circuits (>50amp), often connections in the transformer compartments are a PIA. Thats where a wireway comes i handy.
 
I think it might depend on the circuit size. On larger circuits (>50amp), often connections in the transformer compartments are a PIA. Thats where a wireway comes i handy.
I see. Are the lead wires long enough to leave the wiring compartments, pass through nipples, and make splices? That hasn't been my experience.

Last time I wired BBs was about a year ago, where I added a third unit to convert an existing boost set-up from open delta to wye for a new machine.

The two were side-by-side next to the panel. I cut another EMT to match, added the third, rewired everything, feeding the wires from unit to unit.
 
Last edited:
... we are boosting the utility that changed from 240 delta to a 208 wye . Everything would love a little high voltage at this point. Some of the older rides are straight 230v . Also the area is seasonal and tends to brown around 4pm to 7pm , (that’s a different elephant). It’s a bit to keep it straight some times because on top of it , there are rides imported from Europe that run on 400 volts . The boost transformers are 15% I believe. Three small ones .

Do the rides need 120V for lighting and/or other purposes, and were they previously served from a 240V high-leg delta? You'll be getting 138V L-N after boosting a 208V wye up to 240V. Of course you can still get 120V directly from the unboosted 208V wye source.
 
Synchro , that’s an excellent point , the power is split between motive 3 phase and that’s was our main concern , control and that has an electronic transformer you put anywhere between 100v to 200v you get 24volt out and lighting i believe is a magnetic transformer and I’m going to look into that , hopefully not that big of an issue. As for the method, by the time I got on site ,our guys had done a excellent job running the flex between them . I could not have done better Or prouder . We used 8 awg and the tails didn’t leave the compartment So feeding thru was the best option . You replace one ,you replace all. not that familiar with doing BorB what I did know was a while ago doing yogurt machines I think the voltage had to be close to the manufacturer specs. Didn’t last long but soft serve yogurt was everywhere for about a year then died.
 
I don't have an issue with liquid tight of some sort. Who cares what it looks like. it is functional.
What about using two T-condulets and one LB (or LR or LL) to connect the vertical stack?

All of the connections can be made within the transformer wiring compartments.
I thought about that but use T’s instead, they where done by the time I got on site and look good using 1/2” flex.
 