building calc

Status
Not open for further replies.

OOAC

Member
Location
el paso tx. usa
Design build project : (1)two story bldg with total 16aptment units each with aprx 690sf all gas, and with one common landry room andone common twin CITYMULTI heat pump 10ton mca 45/42, mocp 60. and 6ton mca 25/23, mocp 35, 3ph 208/230v; each appartment with (3) wall mount air blower NO em heat, 208/230v, mca.19a, mocp 15a.
need to calculate for just ONE service size for thebuilding each appartment: living,kitchen,bathroom and two bedrooms
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
need to calculate for just ONE service size for thebuilding each appartment: living,kitchen,bathroom and two bedrooms
OK. You need to calculate. Is there a question? We are not going to do the calculation for you. Have you tried to do the calculation, and have you run into questions or problems? Tell us what you have done, and then perhaps we can help.
 

OOAC

Member
Location
el paso tx. usa
690sf * 3va = 2070va
2070va/120v=17amp or (2) 15a cir
small appl=(2) 1500=3000
-------
5070va
3000@100%=3000

2070 @35%= 325
------
3325va/(208v)(1.732)=total load ? 10amp per unit * 16 = 160amp
 