?If the customer owns a padmount transformer, 12.5kV-480/277v, how is the service to the building grounded? The transformer is outdoors and feeds a main distribution switchboard. Do we bond the neutral at the transformer only, or at the switchboard and transformer??
The difference of WHO owns the transformer is immaterial to the installation.
Nunu161
?..Then he had us bond the neutrals and the egcs in both the transformer and the MDP??
I Agree with the engineer, sorry.
Don, Illinois
? In this case the conductors from the transformer are feeder conductors and not service conductors.?
The difference of WHO owns the transformer is immaterial to the installation.
This makes the feeder conductors Service conductors.
"The earth shall not be considered as an effective fault-current path".
True, but that does not stop it from being one.
My Reference may be old but so am I.
Stallcup?s 2002 changes pg 2-61
Stallcup, Designing Electrical Systems 1990 Code pg 182
Mike Holt , Bonding Neutral Vol 5, #4 p119 [has diagram]
Americans Electricians Handbook, 13th edition pg 3.7
Service Equipment is the necessary equipment, ? that is intended to constitute the main control and means of cut off of supply.
Industrtial and Commercial Power Distribution, 1995 chapt. 10
?The System of Secondary Circuits beyond those transformers normally supplied by a utility and provided with independent overcurrent protection are considered Separately Derived.?
With 37 acres of property, 23, 2500KVA 12.5/480 transformers.. all above issues were raised by 3rd Party inspection firm in 2006. Taken to state level.
The determination was: Regardless of who owns the equipment, even if it is an SDS, an outdoor transformer supplying a structure SHALL follow 250.24(2).
EQUAL POTENTIAL GROUNDING --- REQUIRED FOR UTILITY--- FAULT VALUES