snjeza said:Does equipment grounding conductor has to be run in each raceway together with phase conductors? Can each peace of equipment forming the circuit be separately grounded to the building grounding grid and not having equipment grounding conductor in the raceway?
A connection to a grounding grid does not take the place of an equipment grounding conductor.it's a power plant and they usualy use grounding grid to ground equipment.
don_resqcapt19 said:A connection to a grounding grid does not take the place of an equipment grounding conductor.
Don
don_resqcapt19 said:A connection to a grounding grid does not take the place of an equipment grounding conductor.
Don
I stand by my statement. The conductor you are talking about is not an EGC. The code does not permit a connection to a grounding grid to replace an EGC.I have seen, and grounded many a xfmr, switchgear, and the like by means of connection to the ground grid.
Yes, the NEC requirements for equipment grounding are the same for grounded and ungrounded systems.Don, if this is an ungrounded system, is an EGC still required to be run with feeders and branch circuits?